Update on the Onan error codes:
Ray, thanks for the service manual link. It'll come in handy.
Rich, I did visual inspection and all looked OK. New oil and filter and started but got the same error codes.
Found a procedure to reset the codes. I'm having trouble with the link, so here's the procedure that worked for me:
Turn off the breakers on the generator
On the generator push STOP twice rapidly, followed by one rapid push to START. Do not start the generator.
Hold,down Stop/Prime and it should show a steady red light. If not, repeat the procedure.
If there is the steady red light on Stop/Prime, start as usual. Once it's up and running, turn on the breakers.
The procedure worked. Genny started and I let it run for 5 minutes or so and turned on the breakers. Turned on the a/c to load it up and let it run. All good, no error codes!