I was ready to have my basement unit pulled out because of poor cooling. I had already replaced two start capacitors (one was fried, preventing #1 compressor from coming online).
Still wasn't cooling properly. But others on this forum convinced me to check the ducting coming out of the basement unit, and up in the rear cap area. Yup, that was it: there was a duct leak, shown below at the bulge (I'm on my back, looking up; rear cap is to the right).
The fix was to apply metal (NOT regular cloth) duct tape to seal the leak:
I used a 4 or 5 ft 1"x3" board to apply the metal tape:
It worked, and only cost pennies. I submit this only if you have a duct leak (and in the lower part of the duct). If it's something with the compressor, that's 'nother story.
Thudman