Quote:
Originally Posted by Morich
Jet me check if I am actually getting what you are doing?
You have a gauge just before the generator to measure the gas pressure and it goes to zero when the generator is running and then the generator dies?
Since the regulator is meant to keep the pressure steady under all conditions, that certainly does sound like the new one has failed!!
One odd thought might be if the pressure comes back up after the generator has died
? That might say the gas line and new reg are not passing the enough gas volume to keep the line filled to let the gen. run?
Might want to double check the reg is correct for both pressure and amount of gas it passes?
Not really gas trained here, so just thoughts to pass think over?
|
Yes, shortly after the generator starts the pressure drops from what it should be, 11WC to around zero. Sometimes it bounces around a bit - which causes the generator to surge, but then the pressure goes back to zero. As soon as the generator quits entirely, it returns to 11WC. As confirmation that the pressure is going down, we lit the stove one time before starting the generator, after attempting the generator start the stove was no longer lit.
I had replaced the regulator in April with a new OEM one:
https://www.amazon.com/Capacity-Stag...815715&sr=8-13
400k BTU. Before doing that, I had ordered a cheaper one (only rated at 160K BTU) from Amazon. I'm going to swap the cheaper one in it today. Despite the insistence of the guy at the RV repair shop that I should use the OEM one, it does appear to me that 400K BTU is overkill. A 2.5KW generator implies a 5 to 8HP engine, and this site:
https://www.primalsurvivor.net/propa...on-calculator/
implies you only need about 10K BTU Per HP.
The gauge I got off of Amazon, and it is installed directly into the propane distribution manifold (there was one spare port). What is strange to me is the fact that it seems to supply enough LP for the Truma and stove (both at the same time) but the generator kills it. The April failure resulted in the Truma and generator not starting, and only a very tiny flame from the stove.
BTW, the generator worked fine after the current regulator was replaced, and I just noticed an issue last week while checking it before our most recent trip. It was hard to start then, but would start and run until the load was turned on, which would tend to cause it to die (most of the time). As of yesterday, we've progressed to a situation where it dies within a few seconds of startup.
If the OEM regulator failed again after just 12 days of camping this year, I'm going to be really pissed - but OTOH at least it is a failure I can diagnose and fix myself. It is really masking a generator issue, I'm in trouble. All the shops around here tend to be scheduling many months out!
Thanks