Quote:
Originally Posted by sgtstriker
Glad to see this thread... I have paid to replace the circuit board and thermostat, then the capacitors and relays. Now I have had an entire new unit put in at >$4000
When I went to pick it up I wanted to ensure that it was finally a working A/C system.
I started the gen, waited, and then turned the A/C on to "cool" and "Hi fan" Nothing happened for about 4 minutes, then the fan and Comp#1 came on and about 90 seconds later comp#2 came on.
In the past it seems to me that the fan came on immediately when I turned on the A/C and comp#1 came on after maybe a minute.
Is there a reason that nothing would happen at all for 3 - 4 minutes when I turn this brand new A/C on? (I did this cycle 4 times and the delay was about equal each time).
I don't want to pay these guys again if it is not working as designed.
|
Here is the sequence for my 2004 service manual from RVP. Since you have a new replacement, it could be somewhat different.
8. A TYPICAL COOLING CYCLE OF THE HEAT PUMP
Begins with a call from the wall thermostat for High or Low fan
(customer choice).
Indoor fan starts on the selected speed.
Within a few seconds the thermostat will call for cooling.
Compressor 1 starts.
Outdoor fan starts 2 seconds later (Low Speed).
1 minute later the thermostat calls for second stage cool
(subject to 2 degree temp. differential).
Compressor 2 starts, the outdoor fan goes off (subject to
available 115 volt power supply).
Outdoor fan starts again 2 seconds later (High Speed).
Both systems operate to satisfy the thermostat.
Both compressors shut off at setpoint temperature.
When the thermostat calls for cooling again it will start by
calling for stage one only.
If the heat pump is unable to keep up with the load, stage 2 will
start again when the indoor temperature is 2 degrees above the
setpoint.