Cummins energy command 30 problem

I have a question regarding the auto start on my Cummins energy command 30. I have a 2013 Winnebago Tour QD. the auto start has worked fine until this year. When I set it recently, I was connected to 50 amp service. There were no problems with the power supply, but when the auto generator was engaged with the air units running, the auto setting would start the generator. When the air is off the auto set does not start the generator. I've tried this on two trusted power supplies and the same thing occurs. Any advice would be greatly appreciated
77littledoc is offline   Reply With Quote
Old 04-07-2015, 05:42 PM   #2
Winnebago Master
 
bobmac's Avatar
 
Join Date: Mar 2008
Location: Southern Ontario
Posts: 562
Best thing you could do first is google and download the Cummins EC-30 manual. Winnebago did not include it with my coach so I assume you do not have it either. The EC30 will start the generator - when it is set to Auto - on one of three conditions - battery voltage, a call for AC from the thermostat or the loss of shore power. You need to program the parameters for the EC30 to start and stop as detailed in the manual.
It should not start the generator if the coach is connected to shore power and it has been properly wired. Winnebago wires a sense lead to an AC power circuit in your coach to insure it doesn't start with shore power present. You might want to make sure all of your AC breakers are on in case the sense lead is fed through one of the circuits that is off. If that doesn't fix the problem, you will likely need to call Winnebago to determine where the sense circuit (often a 12+v door bell transformer) is connected in your coach. Your problem sounds to be with the sense circuit that is not telling the EC30 that you have shore power. Good luck,
__________________
Bob
09 Journey 39Z
Southern Ontario
bobmac is offline   Reply With Quote
Old 04-07-2015, 06:58 PM   #3
Winnebago Camper
 
Join Date: Jun 2012
Location: CRAWFOD GA
Posts: 5
I downloaded manual but did not see a way to reprogram. Hopefully Onan in Elkhart can help.
77littledoc is offline   Reply With Quote
Old 04-07-2015, 07:58 PM   #4
Winnebago Master
 
bobmac's Avatar
 
Join Date: Mar 2008
Location: Southern Ontario
Posts: 562
77littledoc:
I would get them to check the "doorbell transformer" that should be connected to a "non-inverter" circuit so it will sense AC failure. Evidently, these transformers fail and the generator then starts regardless of shore power. With a failed transformer, the AGS believes shore power is not connected. That sounds like your problem. Should be a simple fix if they can find the transformer but Winnebago does not seem to show it on wiring diagrams but should indicate where it is if they call them. Good luck,
__________________
Bob
09 Journey 39Z
Southern Ontario
bobmac is offline   Reply With Quote
Old 04-08-2015, 07:51 AM   #5
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,468
77littledoc, the "doorbell transformer" for shore power sensing on your coach is connected to the WASHER breaker, make sure it is not tripped or turned off. It is connected to the back of the breaker panel.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 04-08-2015, 06:58 PM   #6
Winnebago Camper
 
Join Date: Jun 2012
Location: CRAWFOD GA
Posts: 5
Thanks to the wisdom and experience of the helpful members my problem is solved. The water heater breaker next to the washer breaker was tripped. Reset that breaker and all is working fine. I had talked to Winnebago and Cummins support with no help except to drive 100 miles to Cummins south in Atlanta for diagnostics. My common sense antenna believed something simple was the problem. In fairness the Onan tech in Elkhart was on vacation. He is supposed to be very knowledgeable. I am very happy to have had the help of irv2 members.
77littledoc is offline   Reply With Quote
Old 04-08-2015, 09:11 PM   #7
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,740
GREAT troubleshooting guys. This is good to know. I have not had a problem but one never knows.

Rick Y
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Reply

Tags
cummins


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installation of Onan Energy Command in Adventurer bsmith8 Winnebago Class A Motorhomes 87 09-15-2008 03:25 PM
Energy Command 30 Installation arkaussie Electrical | Charging, Solar and Electronics 6 10-23-2007 02:02 PM
Energy Command 30 hogbreth Electrical | Charging, Solar and Electronics 8 03-05-2005 01:19 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.