Furnace problem
We have a 2012 35' Winnebago, Vista. The propane furnace will not come on. It was working fine, then suddenly, when I turned the thermostat to gas heat, nothing. It makes a click from the unit, but that is all. We flipped all the breakers, but I do not see one that says furnace, heat pumps, but no furnace. The tech at Camping World said to check the fuses. Where are they? The books we have do not show fuses. I hope this is something simple. Just hate to drive it to a service dept. when it may be something easy! Any info would be much appreciated.
|
|
|
01-17-2014, 08:42 AM
|
#2
|
Winnebago Camper
Join Date: Apr 2012
Location: Louisville, KY
Posts: 25
|
How cold is it? Propane won't flow at really cold temps.
__________________
Mark Anderson - FMCA 351514 - Louisville, KY
2007 Sportscoach Pathfinder 377DS - Freightliner XC
2006 Jeep Commander
Cricket SW3 Personal Transporter
|
|
|
01-17-2014, 08:45 AM
|
#3
|
Winnebago Camper
Join Date: Apr 2007
Location: SW FL
Posts: 27
|
Quote:
Originally Posted by topdownman
How cold is it? Propane won't flow at really cold temps.
|
X2 and does the stove light? Make of furnace will also help with problem solving. That same furnace was installed in several manufactures MH's. Many may have the same brand of furnace and be able to help troubleshoot the problem.
__________________
Chuck in SW FL
A "Classic" 2014 Entegra Anthem 42RBQ
2016 Colorado Z71 PU
|
|
|
01-17-2014, 08:45 AM
|
#4
|
Winnie-Wise
Join Date: Aug 2009
Posts: 307
|
Welcome to the forum. I've moved this to our Winnebago section hoping another member with a similar coach can assist.
Cliff
__________________
[SIGPIC][/SIGPIC]
Cliff,Tallulah and Buddy ( 1999-2012 )
|
|
|
01-17-2014, 08:56 AM
|
#5
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
not that cold, 40's, the propane will light the stove, fridge, water heater.
|
|
|
01-17-2014, 08:57 AM
|
#6
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
Quote:
Originally Posted by brobox
X2 and does the stove light? Make of furnace will also help with problem solving. That same furnace was installed in several manufactures MH's. Many may have the same brand of furnace and be able to help troubleshoot the problem.
|
everything else propane lights
|
|
|
01-17-2014, 08:58 AM
|
#7
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
Quote:
Originally Posted by muddcatt
everything else propane lights
|
it is a Suburban furnace
|
|
|
01-17-2014, 10:53 AM
|
#8
|
Winnebago Master
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,470
|
The breaker for your furnace is in the group of breakers at the All-In-One panel.
It is on the left side bottom row labeled, Front Furnace/exit fan.
I assume the fan is not running.
Check the connectors at the thermostat and furnace.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
|
|
|
01-17-2014, 11:41 AM
|
#9
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
Thank you. It was not tripped. I will check the connections
|
|
|
01-17-2014, 02:01 PM
|
#10
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
Quote:
Originally Posted by muddcatt
Thank you. It was not tripped. I will check the connections
|
The connectors look fine
|
|
|
01-17-2014, 03:01 PM
|
#11
|
Winnebago Master
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,470
|
If you have a meter check the following at the furnace plug.
Pin 1 wire JM is GND
Pin 2 wire JJ is Call for heat from thermostat
Pin 3 wire JB is +12VDC power to furnace
If you have power on both pin 2 and 3 then it is something in the furnace.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
|
|
|
01-17-2014, 05:52 PM
|
#12
|
Winnie-Wise
Join Date: Apr 2012
Location: Southern NM
Posts: 327
|
Does the fan come on when you turn on the gas heat?
__________________
2014 Phaeton 40 QBH
2015 GMC Sierra SLT 4x4
|
|
|
01-17-2014, 08:03 PM
|
#13
|
Winnie-Wise
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 432
|
Quote:
Originally Posted by topdownman
How cold is it? Propane won't flow at really cold temps.
|
Pure propane goes to atmospheric pressure (0 psig) at -40 degF. I doubt if it is that cold. If there is some moisture or oil in the regulator, it can freeze in the regulator.
If you can light the stove top burners, it is not a propane flow issue.
Your normal start sequence for a propane furnace is the blower will come on first to clear the combustion chamber. It runs for a given amount of time and if the sail switch is made, it will open the gas valve and the ignitor will fire. If a flame is detected by a temp/flame sensor, the unit will stsrt to heat. If no flame is detected, it will continue to run the fan and cycle through another ignition sequence. Normally, the furnace will try to ignite 3 times, before it locks out the gas valve. Some will let the furnace fan continue to run with no heat. To get the furnace to try igniting again, you will need to cycle the furnace off and then restart the furnace.
If your fan is not starting at all, you need to start by checking power to the furnace.
Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
|
|
|
01-18-2014, 10:18 AM
|
#14
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
no fan..nothing
|
|
|
01-18-2014, 10:21 AM
|
#15
|
Winnebago Camper
Join Date: Jan 2014
Posts: 13
|
Thank you, Ken. The fan does not come on so it sounds bad connection or like you said restart...we will try these things
|
|
|
01-18-2014, 01:14 PM
|
#16
|
Winnebago Camper
Join Date: Mar 2011
Location: Central Texas
Posts: 5
|
Quote:
Originally Posted by grtharris
If you have a meter check the following at the furnace plug.
Pin 1 wire JM is GND
Pin 2 wire JJ is Call for heat from thermostat
Pin 3 wire JB is +12VDC power to furnace
If you have power on both pin 2 and 3 then it is something in the furnace.
|
Muddcatt, did you check as above for power?
ronspradley
__________________
1993 Gulfstream Sun Voyager DP 30'
200 HP Cummins B5.9, 4sp Allison AT542
Toad 1998 Honda CRV, 2006 Honda CRV
Life's too short to drink cheap beer.
|
|
|
01-18-2014, 02:38 PM
|
#17
|
Winnie-Wise
Join Date: Jan 2012
Location: Cincinnati
Posts: 486
|
Does the wall thermostat still work to turn on air conditioner? If so, we can assume (maybe wrongly, but more later) it is sending start signal to the furnace. As TXiceman said, once the signal is sent, the fan should come on. Moving air then pushes on the sail switch which tells circuit board it's O.K. to open gas valve and ignite. If the issue is not in the thermostat or fuse to furnace 12 v power, the next thing is to suspect the fan motor. You can access the wiring through the outside hatch. Test for power here and also see if there is a switch, fuse, or circuit breaker in the access door.
If you have power here, it's either the thermostat not sending a signal or a failure of the control board.
__________________
Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
|
|
|
01-18-2014, 06:59 PM
|
#18
|
Winnebago Owner
Join Date: Dec 2010
Location: DW Driver -Winter Englewood FL, Summer Willingboro NJ
Posts: 116
|
off on switch
By now you know how it works but there is an off on switch (at least on mine) found on the left hand side of the furnace. It trouble shooting found on line states clearly in several areas, that the power from the thermostate go to the off on switch.
The wall thermostat controls the operation of the dual stage furnace by reacting to room temperature. This allows current to flow through the On/Off switch to the Blower Speed Control Board then to the Module Board.
How do I know this, experince on a cold autum night. Mine would not start but I tore into the unit and found this switch. it was in the on position but after I acutated the switch a few time it worked. I also believe it reset something on the board. It has worked well ever since and that was two years ago.
__________________
La Dagobago
99 36 FL Winne Chieftain 5.9 ISB Turbo Cummins DP, 24' box with 1972 V12 XKE Jag and HD Sporty Hobby of 1970's Suzuki dirt bike restoration. Visit my blog.
|
|
|
01-18-2014, 07:10 PM
|
#19
|
Winnebago Owner
Join Date: Sep 2012
Posts: 60
|
Unless you can check 12VDC systems then you really can't do anything. They aren't hard to learn, if you want to.
It also wouldn't heart to learn the difference between "breakers" (commonly 120VAC) and fuses (commonly 12VDC).
|
|
|
01-18-2014, 07:14 PM
|
#20
|
Winnebago Master
Join Date: Sep 2005
Posts: 962
|
Help me here ... can't he jumper two wires on the thermostat to see if the problem is in the furnace or in the thermostat?
I think that is possible ... but I don't know which two wires he should jumper
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
Similar Threads
|
Thread |
Thread Starter |
Forum |
Replies |
Last Post |
Furnace problem
|
harry t |
General Maintenance and Repair |
13 |
02-03-2008 03:08 PM |
Gas furnace problem
|
Toole'n Along |
Winnebago General Discussions |
7 |
01-27-2008 09:27 AM |
Another LP Furnace problem...
|
Moder2 |
General Maintenance and Repair |
26 |
12-19-2007 06:19 AM |
Furnace problem
|
Doug Sage |
General Maintenance and Repair |
10 |
11-23-2007 02:37 PM |
Furnace Problem
|
JJ Hamick |
General Maintenance and Repair |
6 |
10-22-2006 01:57 PM |
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|