Old 12-19-2022, 01:55 PM   #1
2002 chieftain 36w
 
Join Date: Nov 2022
Posts: 18
Plugging into house outlet questions?

I'm going to be parked at a friend's house in a few weeks. He says he has an electric dryer outlet that is 120v with a 40amp breaker. He says I can plug my 50amp rv into with an 50-15 adapter. Is this right I know I can't plug into a 30amp dryer plug in. Sorry if this has been aske,, but I searched and didn't see it.

I have a 2002 chieftain 36.
Timo1 is offline   Reply With Quote
Old 12-19-2022, 03:05 PM   #2
Site Team
 
Eagle5's Avatar
 
Join Date: Mar 2019
Location: South Bend, WA
Posts: 2,766
Hi Timo1,
Something seems sort of odd about a 40 amp dryer breaker. My home dryer runs on the twin-phase 30 amp circuit, the current version of that 30 amp plug looks like this:



The standard Twin-phase 50 amp RV outlet looks like this:

A 15 amp outlet is just a regular household outlet. Do you have one of those adapters?

Eagle5
__________________
2019 Minnie Winnie 22M on an E-450 frame
Eagle5 is offline   Reply With Quote
Old 12-19-2022, 03:30 PM   #3
2002 chieftain 36w
 
Join Date: Nov 2022
Posts: 18
Yes I have that adapter. I'm using it right now at my house. My friend says his dryer is plugged into a normal looking outlet not the 30amp outlet you have pictured.
__________________
2002 chieftain 36w.
Timo1 is offline   Reply With Quote
Old 12-19-2022, 06:44 PM   #4
Winnebago Master
 
Join Date: Nov 2018
Location: Pflugerville/Austin, Tx
Posts: 8,613
One way this might get done if the drier is gas, it may be a case where somebody lacking knowledge converted a 220 plug to "normal" 110 plug for the electrical supply.

Possible a 15-20 amp outlet breakered to 40 amp?

Aproach VERY carefully!
__________________
Richard
Why no RV year, make and floorplan on MY signature as we suggest for others?
I currently DO NOT have one!
Morich is online now   Reply With Quote
Old 12-19-2022, 10:31 PM   #5
Winnebago Master
 
Wayne M's Avatar
 
Join Date: Aug 2008
Location: Texas
Posts: 1,678
Agree, but not only approach cautiously, meter the receptacle.
__________________
Wayne MSGT USMC (Ret) & Earlene (CinCHouse)
2015 Winnebago Tour 42QD - 2020 Lincoln Nautilus Reserve (TOAD)
(RVM-14) It is what it is, and then it is what you make of it.
Wayne M is offline   Reply With Quote
Old 12-20-2022, 02:25 PM   #6
Winnebago Master
 
bigb's Avatar
 
Join Date: Apr 2018
Location: Tucson, AZ
Posts: 1,441
Lot's of homes have a 240V dryer circuit in addition to a gas hookup and the required 120V 20 amp laundry circuit. As far as an electric dryer that is 120V, they make them but they are on a 20 amp circuit and extremely rare as they take eons to dry a load. A 15 or 20 amp outlet cannot be on a 40 amp breaker. My guess is your friend is mistaken, either the dryer is gas which also has a 120V plug for the motor & timer or he is looking at the washer plug and missing the dryer plug. Another possibility is there is an unused dryer circuit but it should only be on a 30 amp circuit unless it was installed or modified by a non-qualified person. A career in the electrical trade taught me that more often than not the panel labeling is incorrect and should never be taken as the truth.
If there is indeed a 20 amp receptacle on a 40 amp breaker (which I doubt), even if the wire is sized accordingly the receptacle will easily melt down when overloaded.
__________________
Brian
2011 Winnebago Via 25Q on 2010 Sprinter Chassis
bigb is offline   Reply With Quote
Old 12-20-2022, 02:45 PM   #7
2002 chieftain 36w
 
Join Date: Nov 2022
Posts: 18
Yep after my friend looked closer after I forwarded this thread to him. His dryer is gas and the 40amp breaker is no longer hooked up to anything(electric dryer was removed years ago). The washer and dryer are plugged into the same outlet cluster that must be 20amps or maybe 15amps.
Timo1 is offline   Reply With Quote
Old 12-20-2022, 03:01 PM   #8
Winnebago Master
 
Join Date: Nov 2018
Location: Pflugerville/Austin, Tx
Posts: 8,613
So many things that are wrong with the info given that there isn't really a place to start on getting it done right.
IF the outlet is a standard 110 outlet, it should be breakered no more than 15 or possibly 20 if the corrrect outlet is used.
But IF it is a standard 15-20 amp outlet and IF the breaker is okay at 15 or 20 amp, that still leaves it true that you can only get 15 amps out IF you are doing it reasonably safe.
That will limit you to Airconditioner being unlikely but "Might" run. I would not plan on it. Lights and battery charging is likely okay. Microwave likely okay but not at the same time as other high currrent uses like a hair drier.

So I might guess you CAN plug in and do a few of the basics but not something I would recommend for very long term and certainly not without checking for sure what they have as what you have told us so far sounds really confused or bad!
The point to look for is what is the lowest rated item and one of those we know about will be the 15 amp adapter.
It can appear to be working fine, but it can just be heating up and getting ready to fail!

EDIT!
Whoops, sorry about my post. I was typing while you were updating the info!
__________________
Richard
Why no RV year, make and floorplan on MY signature as we suggest for others?
I currently DO NOT have one!
Morich is online now   Reply With Quote
Old 12-20-2022, 03:53 PM   #9
Winnebago Master
 
bigb's Avatar
 
Join Date: Apr 2018
Location: Tucson, AZ
Posts: 1,441
Quote:
Originally Posted by Morich View Post
IF the outlet is a standard 110 outlet, it should be breakered no more than 15 or possibly 20 if the corrrect outlet is used.
A common mis-conception. An ordinary 15 amp duplex can be legally and safely used on a 20 amp circuit, they are both rated at 20 amps. The only difference is the face configuration, the 15 amp does not allow a 5-20P to be inserted so that a device that requires a 20 amp circuit cannot be plugged into a 15 amp circuit. It is however, illegal to install a 20 amp receptacle on a 15 amp circuit for obvious reasons.
__________________
Brian
2011 Winnebago Via 25Q on 2010 Sprinter Chassis
bigb is offline   Reply With Quote
Old 12-25-2022, 04:53 PM   #10
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,740
Quote:
Originally Posted by Timo1 View Post
I'm going to be parked at a friend's house in a few weeks. He says he has an electric dryer outlet that is 120v with a 40amp breaker. He says I can plug my 50amp rv into with an 50-15 adapter. Is this right I know I can't plug into a 30amp dryer plug in. Sorry if this has been aske,, but I searched and didn't see it.

I have a 2002 chieftain 36.
I'd approach this with great cation. The dryer can not have a standard 15 or 20A plug. The standard dryer is 240V or 120V/120V/30A. This can be 3 or 4 wire. The 4 wire setup provides L1, L2, N and G (120V/120V). The 3 wire setup is only L1, L2 and ground (240V). The 240V outlet will fry your rig. You must have a Neutral for your RV to have proper power with either 30A or 50A service.

I do not recommend using a 15A outlet ever. You can get away with a 20A outlet for charging your batteries but the adapter must be watched for over heating. Because many chargers draw 12 to 15 amps a 15 A circuit would be pushing its limit. 80% load is all that is allowed in code. This is to prevent fires.
Best of luck.
Rick
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 12-27-2022, 12:55 PM   #11
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,376
Everything is explained in detail here: https://www.myrv.us/electric/
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Old 12-28-2022, 04:42 AM   #12
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,740
Quote:
Originally Posted by Ray,IN View Post
Everything is explained in detail here: https://www.myrv.us/electric/
Nice find, Ray. Very detailed by simple explanation of the RV outlets. From some of the sad stories I have see on the forums I think a few electricians need to review there knowledge of RV service before installing a 30A service. Too many, even though few, have wired them for 240V! OUCH!!!!
Happy New Year,
Rick
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 12-29-2022, 09:21 AM   #13
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,376
Jerichorick we refer to that website frequently over on irv2.com and the Winnebago forum.
It's indisputable information for correcting new RVers and some uninformed electricians.


This little-sister website does not usually get the benefit of older members of RV Life, as we are attached to the original website.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rear lights out after plugging in tow dolly ZimBob Electrical | Charging, Solar and Electronics 6 10-10-2021 11:33 AM
Plugging in to house? Micro Minnie 1808FBS Ponder Electrical | Charging, Solar and Electronics 9 07-01-2021 07:58 AM
Plugging in Rmoe3 Electrical | Charging, Solar and Electronics 3 03-13-2018 07:27 AM
Wil spare tire fit into basement storage compartment? Catpowered Running Gear, Axles, Brakes, Wheels and Tires 17 11-25-2008 02:30 PM
Plugging into 110 with coach batteries removed Nonno Electrical | Charging, Solar and Electronics 18 12-31-2006 11:10 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.